Todd
With your PV on a dwelling unit, you should have Ground Fault Protection on it. A common place to install this is in a DC load center.
You should also have a DC disconnect. Your remote on/off switch for the inverter does not count as a disconnect.
You might want to download the Xantrex manual on PV fault protection, and read it. There are some good diagrams.
http://store.altenergystore.com/Enclosures-Electrical-and-Safety/Miscellaneous-Electrical-Parts/Ground-Fault-Protection/Xantrex-Pvgfp1-Ground-Fault-Brkr-100A-122448V/p2202/
Then ask any additional grounding questions that you may have.
Your current bonded grounding rods can take both the ac and dc grounds.
Yes, your ac neutral should be bonded to ground at some point downstream of the inverter.
I didn't see (and you have not mentioned) any ac overcurrent protection. I am hoping that you have at least an inline fuse, somewhere.
Ken