Max Lead Acid Discharge Current.

Posted by Jerry Wenzel on July 28, 2008, 06:06:51 PM

Re: Max Lead Acid Discharge Current. (Reply #5)
Ken,

I calculated my watthour/day usage from the wattage of the load times the number of hours I expected that load to be on.  That's where the 750 watt hours came from.  I don't expect to draw peak current during normal daily use.

I didn't do a good job of explaining why I'm asking about the high 200A+ currents.  My inverter is 2000W with a 4500W surge.  I rarely expect to draw 1500 or more watts.  However the inverter is capable of drawing 200A to 400A from the batteries if enough AC load is turned on. 

I wanted to make sure I didn't damage the batteries if someone turned a microwave and toaster on at the same time, or plugged in a larger power tool.  I'd rather the batteries and DC cabling could handle an occasional high current instead of blowing a fuse or breaker or damaging a battery.

I looked through my inverter manual (Xantrex Prosine 2.0) and don't see a setting setting for max DC current draw.  I need to enter the battery type, but that appears to be for charging use not limiting maximum discharge current.

This is a weekend cabin and will generally only see load 2 days per week.  I planned on sizing the solar panel(s) to take 2 or 3 days to fully charge the batteries after a weekend of use.  I also have a 3000W generator, but would like to minimize its use.

Your comments on the discharging the batteries too much are well taken.  I was thinking I might be discharging the 2 GC2 batteries too much.  For a bigger bank, 4 golf cart batteries or 2 L16 batteries cost about the same.  I'm thinking 2 L16s are a better/simpler solution.

Any thoughts on sizing the batteries and DC supply system to take the loads of high unexpected AC usage?

Are 2 L-16s in series better than 4 GC2 in a series/parallel connection?

Any recommendations on battery manufactures?  Trojan and Crown seem to be popular.

Thank you for your patience! I'm new to off grid power.  I'm enjoying the learning and appreciate the help.

Jerry
 

Posted by James Cormican on July 28, 2008, 06:41:24 PM

Re: Max Lead Acid Discharge Current. (Reply #6)
okay, i have to jump in at this point, i cant resist.

for practical purposes of safety we will assume the max current available from the battery will be infinity - for human purposes.  shorting straight across the battery bank can be lethal.

here are the common questions related that I often answer to the best of my knowledge.  i am by no means any ultimate authority, so forum faithful, please check in to factcheck, lest i lead anyone astray.

if the question is actually:  my inverter has a surge of X, will surging it to X hurt my batteries?

then the answer is usually no.  a surge load, typically an inductive load is by nature something that may "surge" for a SHORT (less than 1 sec usually) period of time as it gets going.  motors, compressors, are the usual culprits.  remember the difference between power and energy.  watts x time = energy.  so 4000w x < 1 second = lots of power, not very much energy.  batteries store energy, and will not be affected by this short burst.  were this burst to last for any actual time, then it would deplete the batteries.

if the question is more like:  my inverter has a surge of Y, will surging it to Y hurt my inverter?

well no.  but this is like the price is right.  just dont go over.  and if you are not SURE of  the surge on your inductive load, dont run it, unless you are willing to sacrifice your inverter to find out.  many inductive loads can surge from 3 to 7 TIMES normal running wattage upon startup. 

lastly the question may be:  my inverter has a surge of Z, will surging it to Z be too much for the wires i have connecting the battery bank to the inverter?

good question.  surprisingly, the code does not care about the surge of an off-grid inverter.  if the goal is to protect the wires, mainly from heat and fire, then even the surge limit if double the normal ampacity that they are used to carrying only lasts for a few short seconds, likely nothing bad will happen as a result.  the equation for sizing battery to inverter overcurrent protection device/ disconnect is as follows from NEC 690.8:

battery to inverter disconnect rating

inverter continuous wattage output / lowest operating voltage x inverter efficency (at that condition)

conductors must be sized to handle a higher ampacity than the overcurrent device applied from the equation above.  see NEC section 310.16 or 310.17.

------------

hope this helps with the discussion and the system in question.

cheers,

james
Alt-E staff


AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
« Last Edit: July 28, 2008, 06:49:31 PM by James Cormican »
 

Posted by Ken Hall on July 29, 2008, 03:39:34 PM

Re: Max Lead Acid Discharge Current. (Reply #7)
I think the 4 GC2’s would be better for your use.  450 amp hours, vs 390 amp hours. Equally important, is at about 62 lbs apiece, they will be easier to lift than the 121 lbs, when you have to change them.  You will probably be changing them often. Until you learn a few “hard to learn” lessons.

An off grid system has to be sized for it’s intended use. It also has to be balanced, batteries, inverter, generation, and USAGE. You are putting a larger inverter on small batteries, with smaller generation, and expecting not to hurt anything when you ask it to do a bigger job than it was sized for.

The fact that you are even considering the possibility of a microwave and a toaster being operated at the same time on this size of battery, suggests that you are in for a “learning experience”.  The best solution would be don’t have either one in the cabin. Second best would be a single outlet, forcing people to switch plugs and preventing simultaneous operation.  Put the refrigerator (assuming its electric) on a switched outlet and turn it off while preparing meals (or other peak periods), to prevent it from kicking on and further peaking the load. Don’t have a convenient plug for that large power tool. Drag out the generator for large loads.

Everyone using the cabin has to be load conscious. Otherwise, they will act like they are at home with an unlimited source.  When you put 2 or 3kWh on a system designed for 1kWh, your batteries will have a short life.

You might want to purchase a Kill-A-Watt meter and put it on some of your appliances and get some hard data as to how much you really use them. Beginners tend to underestimate how much use they actually get. You also learn such things as a 1000W microwave draws close to 1500W. (The 1000W is the output, not the electric draw)

If you size your system for 1kWh, you have to learn to live within that allowance. If living within that allowance is unacceptable, you have to increase the allowance.

If you want more power, do a worse possible estimate. Cabin full of people, extensive microwave, toaster, blow-dryer, and large power tool usage. Then size your system for that.  It will cost more money up front, but changing batteries every 1-2 years is not cheap.

Don’t look at tripping breakers as a nuisance. Tripping breakers in an off grid system is a gentle reminder for everyone, that someone is exceeding your predetermined limits.
 

Posted by Jerry Wenzel on July 29, 2008, 05:11:53 PM

Re: Max Lead Acid Discharge Current. (Reply #8)
Thank you for the feedback.

I like the idea of 1 outlet to limit what can be plugged in.

My philosophy is to make an educated estimate on a system that will provide our off grid power needs.  The support from the community here is definitely helping me become more educated. I know that as I learn I may need to add batteries or more solar/wind charging.  Instead of giving my batteries an early death, I'd rather use the generator to fill in the power shortage until I evolve the system to meet our needs.

Along those lines, I planned on doing the following:

*Educating the family on minimizing power use and hope some of it sticks.

*Monitoring the DOD on the batteries and either shedding load or running the generator to prevent > 30% DOD.

*Recharging the batteries ASAP.  Either solar or generator.

*Limiting the max current the batteries get hit with.

*Checking water and equalizing when needed.

Will doing those things help get more years out of my batteries?

My inverter calls for a 300A fuse/breaker to handle surge loads.  Should I be looking at a 200A breaker, which will limit hitting my smaller battery bank with unexpected surge loads?

Does anyone have any thoughts on whether my process of putting in a estimated system, and filling in with the generator until any shortfalls in the system design are corrected?
 

Posted by James Cormican on July 29, 2008, 05:56:58 PM

Re: Max Lead Acid Discharge Current. (Reply #9)
remember the equation? Wink nec 690.8

continuous inverter output / lowest acceptable dc input voltage x inverter efficiency

in your case, xantrex prosine 2.0,

2000 / 10vdc x full load efficiency 87% (.87)

2000 / 8.7 = 230a --- 250a circuit breaker, -- 300a fuse

here are possible dc load centers that could work

http://store.altenergystore.com/Enclosures-Electrical-and-Safety/Electrical-Enclosures/DisconnectLoad-Enclosures/Dc/Xantrex-Dc250-250A-125Vdc-Disconnect-WEncl/p2086/

http://store.altenergystore.com/Enclosures-Electrical-and-Safety/Electrical-Enclosures/DisconnectLoad-Enclosures/Dc/Midnite-Solar-MNDC250-Mini-250-Amp-DC-Disconnect/p2416/

http://store.altenergystore.com/Enclosures-Electrical-and-Safety/Electrical-Enclosures/DisconnectLoad-Enclosures/Dc/Outback-FlexWare-FW500-DC-breaker-enclosure/p5576/

cheers,

james
Alt-E staff


AltE
"Making Renewable Do-able"
http://www.altEstore.com/

Tel: 877.878.4060 x107  or +1.978.562.5858 x107
Fax: 877.242.6718  or +1.978.562.5854
 
Forums | Design by Scratchmedia | Development by SMF.
© 2001-2005, Lewis Media. All Rights Reserved.

Disclaimer and Disclosure

The Alternative Energy Store, Inc reserves the right, within its sole discretion, to refuse or delete any posting or portion thereof, or terminate or block the access to this forum.

The opinions and statements posted on this forum are the opinions and statements of the person posting same, and do not constitute the opinion or act of the Alternative Energy Store, Inc (AltE). The Alternative Energy Store, Inc does not endorse or subscribe to any particular posting. No posting shall be construed as the act or opinion of the Alternative Energy Store, Inc.

Need help designing your system?
Call Us Toll Free!

877-878-4060

Se habla Español

cart

0 items

 

top members